Be the least expensive option.It is just a run of the mill contactor. You should be able to replace it with just about any brand. Personally I would rip it out and put in an oversized IEC contactor.
I don't know how hard it is to get a 208 volt coil though on any motor starter. It's not real common these days.
You should be able to replace it with just about any brand.
The enclosure doesn't probably care what is mounted in it.Here's a question: This looks like an enclosed starter, not a contactor in some random box. Is there a listing issue with replacing the contactor with something else?
But if the unit is a listed assembly, not just an enclosure? Like if the UL sticker on it says "Enclosed motor starter"The enclosure doesn't probably care what is mounted in it.
The listing has to do with the condition of the equipment when it left the factory. As soon as you put your own conduit it entry into it you may have negatively impacted the equipment, so it is up to the AHJ to approve the installation.But if the unit is a listed assembly, not just an enclosure? Like if the UL sticker on it says "Enclosed motor starter"