Not likely, load neutrals are not usually necessary.Yes breaker neutral landed on neutral buss with neutral from panel. Hot tub is straight 240v no neutral. Could that be causing an issue?
Not likely, load neutrals are not usually necessary.Yes breaker neutral landed on neutral buss with neutral from panel. Hot tub is straight 240v no neutral. Could that be causing an issue?
Worth a try although I do not see how we would have continuity as that neutral would just be tied to the neutral in the hot tub disconnect.Maybe somewhere in the house there are neutrals of different circuits tied together with a wire nut?
Take the neutral from the hot tub off at the panel and see if you have continuity from the disconnected neutral to the the neutral bar in the panel?
No, and in fact eliminates one possible leakage-current pathway.Hot tub is straight 240v no neutral. Could that be causing an issue?
When you ruled out everything that is likely, it's time to check the unlikely. Especially when it's quick and easy to test. It could be something like a nail or screw that Murphy Law drove into a wall.Worth a try although I do not see how we would have continuity as that neutral would just be tied to the neutral in the hot tub disconnect.