JimmysLimeade
EE Student & PV Design
 - Utah
 - PV Design
I am having trouble understanding which ampacity to use when sizing AC wires and I can't wrap my head around it for some reason. Here's an example of what I am having issues with:
I have an inverter with an output current of 42A in an area with an ambient temperature of 35C. There are 3 THWN-2 CU conductors in the conduit from the inverter to MSP. What size of conductor would you use and how do you get to that answer.
The way I have previously done it was take the conductor ampacity in the 90C column and use the derate factors for temperature and current-carrying conductors to get the max conductor ampacity. That number has to be larger than the output current * 1.25.
Using that method, I would get a #6 conductor for this example. But if I used the ampacity at 75C, I would get a #4 conductor. After reading a lot of different ways people get their sizing, I feel like this is the wrong way to do it.
What should I change here? Could someone help me understand what is missing?
Thank you!
Thank you!