Naveen Kumar
- Teaxas, USA
- Student
What is the condition of use (COU) ampacity of 8 #10 CU THWN-2 conductors installed in one conduit at ambient temperature of 35°C?
The question is wrong because it does not tell you the number of current carrying conductors. And what is condition of use (COU)?or the question is wrong?
Yes it does:The question is wrong because it does not tell you the number of current carrying conductors.
It says 8 conductors not 8 CCC's. It could be 6 CCC's which is a different derating percent than 8 CCC's.Yes it does
You're right, of course. My bad.It says 8 conductors not 8 CCC's. It could be 6 CCC's which is a different derating percent than 8 CCC's.
Probably the intent but the question is poorly written.I would work with 8 current carrying conductor's using T310.16, T310.15(B)(1) and T310.15(C)(1)
Absolutely but he may as well figure that way as there is no other way to do it other than configuring it many waysProbably the intent but the question is poorly written.
If this were a multiple choice question to could solve it for every possible scenario and then see if only one of the answers is in the list of choices. If more than one answer is available then the question is unanswerable. Since no list of answers was given I would assume that this is not a multiple choice question.Absolutely but he may as well figure that way as there is no other way to do it other than configuring it many ways
Hi, Thanks for replying guys.
My assumption, for now, is 8 CCC,
Also just neglecting the term "Condition of use". I have no idea about it. Give me suggestions if anyone knows
According to Table 310.16(Cu-THWN2-#10) ampacity is 40
but it has more than 3CCC, so according to "Table 310.15(B)(3)(a)" 8ccc 70% of 40 = 28
Also, ambient temp is 35, so according to 310.15(B)(2)(a) , correction factor is 0.96 of 28 = 26.88
So the breaker should be 30A
I agree. Don't read information into the question that doesn't exist. They asked for the ampacity which is 26.8 amps a 30 amp OCPD may be too large."The breaker should be 30" is questionable.