Hankertonjr
- Nj
- Electrician
Can you sleeve rokex in the exterior chase where hvac line set is ran..trying to save from running conduit.
Seems like Smurf can’t be run exposed if I remember correctly.use smurf tubing
20 + years ago saw a apartment complex in Houston that all the whips feeding the A/C units was ENT. No inspections in the unincorporated area though.Seems like Smurf can’t be run exposed if I remember correctly.
I think it can be exposed if not subject to damage, whatever that means.Seems like Smurf can’t be run exposed if I remember correctly.
Even so, the interior of the ENT will be a wet location per 300.9, and you can't install NM in a wet location.I think it can be exposed if not subject to damage, whatever that means.
Exterior chase sounds like it might be a mini splitexterior chase where hvac line set is ran
And that tray cable is non metallic so it could be confused for romex.Exterior chase sounds like it might be a mini split
If so, is there a factory supplied cable?
Yeppers. "Inside a conduit (etc.)" is not a location. The wires or cables are wherever the conduit it.The discussion of what type sleeve or raceway should have ended when NM was named as the wiring method outdoors.
I did not just read that.........One manufacturer shipped a entire spool of some pretty beefy 14 AWG tray cable with a large order of units.
The inspector was dubious however when shown its from the manufacturer they allow it in the line hide, provided its in the line hide for the majority of the run.
Now they have a updated kind of tray cable with a -JP that is rated for pulling thru joists.
Its easier to strip than UF but you have to tape the orange green
No the interior of a exterior raceway exposed to weather is a wet locationIs romex allowed to be sleeved in pvc on exterior wall?