Transformer Connections
Dwight W
Virginia
Electrical Designer
Hello everyone.
Our drawings show a 225kva, 3 phase transformer 480 pri. / 240, 3 phase Delta sec. feeding a 600A, 240V, 3 phase panel. The contractor is having an issue getting a 240V rated 3 phase panel. He wants to take (3) three 240V single phase panels with MCB and hook them up to the transformer with one panel on A and B, one on B and C, and one on A and C.
In theory this will work. But in section 240.21 (2) and (3) under the tap rules, it states that the secondary conductors shall terminate to a single OCPD. Which means to me that we can provide a 600A fused disconnect to a trough and tap within the trough for the three panels, which meets code. I have been in the trade for 45 years and have never seen anyone take 3 single phase panel feeders to a three-phase transformer.
With that said, does the code allow us to take three sets of single-phase conductors and tap two legs for each panel?
240.21(C) will allow multiple secondary feeds from a transformer to multiple OCP devices.
What are the loads? 240V 2-wire circuits are not common, except for heating.
Yes, the transformer can have (3) separate taps each feeding individual single phase panels with main breakers.
If it is straight 240, you can't use slash rated breakers. Slash rated breakers are more common and cheaper than straight rated ones. Even if there are no 120 volt loads, I would make the secondaries 120/240.
You won't be able to if it is a single transformer built as a 3 phase delta. At best one of your panels might have a neutral if the transformer has a center tap on one winding.
Thank you for the response.
It is actually a welding lab in a community college. With 208V power. The school bought 240V single phase residential welders for students that will not run on 208V and verified by manufacture. We have taken multiple 3 phase panels to a single transformer but have not taken single phase panels to a 3 phase transformer, seems like using different phases it would be considered a double tap. We just wanted a second opinion.
Thanks
Be sure to keep 240.85 (slash rated) {as noted} and 250.21(B) (Ground detection) in mind.
Thanks
The actual transformer connection point is not considered a tap, per article 240, as it is fully rated.
Have you confirmed your welders are acceptable on 240V to ground systems? When I hear residential, I think of 120V to ground maximum.