Jimmy7
- Boston, MA
- Electrician
If you add a subpanel within an existing single family home does it require Surge Protection per 215.18? The panel does not feed another unit, or separate building.
What year code? The 2020 only goes to 215.12If you add a subpanel within an existing single family home does it require Surge Protection per 215.18? The panel does not feed another unit, or separate building.
2023What year code? The 2020 only goes to 215.12
Section 230.67 requires surge protection for services.
Adding a sub panel would not trigger surge protection. IMO
Ron
Thank you.215.18 Surge Protection.
(A) Surge-Protective Device.
Where a feeder supplies any of the following, a surge-protective device (SPD) shall be installed:
- (1) Dwelling units
- (2) Dormitory units
- (3) Guest rooms and guest suites of hotels and motels
- (4) Areas of nursing homes and limited-care facilities used exclusively as patient sleeping rooms
That is my opinion too, but the language could use some work to make that clear.Thank you.
Since the OP is adding a subpanel in an existing dwelling unit, I'm still going to say surge protection is not required.
Ron
Agreed. The code language says that where a feeder supplies a dwelling unit, an SPD is required. The circuit to the sub-panel is a feeder, so it could be implied that an SPD is required. The sticky part is whether the feeder supplies the whole dwelling, or part of the dwelling, it is still "dwelling"That is my opinion too, but the language could use some work to make that clear.
Yes, except in this case, the feeder is not supplying the dwelling. Only a part of it.Agreed. The code language says that where a feeder supplies a dwelling unit, an SPD is required. The circuit to the sub-panel is a feeder, so it could be implied that an SPD is required. The sticky part is whether the feeder supplies the whole dwelling, or part of the dwelling, it is still "dwelling"