I’ve used that one for nearly forty years, works excellent. Very accurate. With two circuits tied together, it splits the signal, so you locate the strongest, turn it off, then the signal will go full strength, then you can locate the second one. Also great at locating the neutral that goes with that circuit, even if a tap was screwed up, and the neutral comes from another panel!Best I've used is the vintage Amprobe CT-326-C Current Tracer. To top Don's experience, I traced from 120V through a 480 xfrm through a 4160 xfrm. Had a situation with a dead receptacle and no breaker handle tripped. Used a battery to create a current loop on the neutral back to ground and traced it to the correct panelboard. In the panel, found that the hot was not hot. The breaker was actually tripped, but the handle hadn't moved to the tripped position!