Because the definition in Article 100 specifies that point of measurement for the voltage to ground on a grounded system as being between the ungrounded and grounded conductor.Why in mike holts definition of voltage to ground the illustration shows the voltage meter between grounded and ungrounded?
Voltage to Ground.
For grounded circuits, the voltage between the given conductor and that point or conductor of the circuit that is grounded; for ungrounded circuits, the greatest voltage between the given conductor and any other conductor of the circuit. (CMP-1)
For most of Mike's examples nominal voltage is all that matters.Ok i just dont like the definition since its more like voltage minus vd and will never be 120v specially when the nec def of ground doesnt reflect this
You have a few days left to submit a Public Input to change the definition. Public Inputs for changes to the 2026 code will be accepted through 5 pm Eastern time, on September 7, 2023.Ok i just dont like the definition since its more like voltage minus vd and will never be 120v specially when the nec def of ground doesnt reflect this
Thank you sirYou have a few days left to submit a Public Input to change the definition. Public Inputs for changes to the 2026 code will be accepted through 5 pm Eastern time, on September 7, 2023.
I’ve never done it.i’ll look into itThank you sir
You have to register with an e-mail address. You go to nfpa.org/70 and click on "submit public input for next edition".I’ve never done it.i’ll look into it
Thank youYou have to register with an e-mail address. You go to nfpa.org/70 and click on "submit public input for next edition".
You need a very good technical substantiation as to why the change should be made.
I don't think from what was mentioned in OP that he is asking about NEC definitions or changing those but rather what Mike Holt has in some publication that was not specifically mentioned.You have to register with an e-mail address. You go to nfpa.org/70 and click on "submit public input for next edition".
It applies to both mike holts illustration and the nec definition. The definition of ground is the earth and neutral is not always grounded or part of ground unless its a corner grounded system Or grounded system. Only when measuring phase to true ground you’ll get voltage close to nominal voltage. Phase to neutral (grounded /grounding as the nec defines it will give you voltage minus vd so it should not be defined as phase to ground. Correct me if im wrongI don't think from what was mentioned in OP that he is asking about NEC definitions or changing those but rather what Mike Holt has in some publication that was not specifically mentioned.
Mike teaches the NEC and will always use the NEC definition for something like this.I don't think from what was mentioned in OP that he is asking about NEC definitions or changing those but rather what Mike Holt has in some publication that was not specifically mentioned.
I don't know the specific document(s) he is referring to, but based on the explanation in OP I am picturing an illustration showing a volt meter connected between a grounded and an ungrounded conductor. Good enough for most general topics. If topic of discussion is a stray voltage type of issue or anything else where one may be concerned with the differential in voltage he most likely would include both grounded conductor and earth ground as well as voltage meter readings between them in the illustration, and pretty much has to to give effective explanation of what is going on in those type of situationsMike teaches the NEC and will always use the NEC definition for something like this.
My comment to the OP was to his statement that he did not like the definition that I posted from the NEC.
I would say it's more the other way around. If, for example, you did not connect the neutral(center of a wye/normally obligated to be grounded) of a transformer secondary to earth, the voltages from each phase to that point would still be the nominal voltage of the secondary. The voltages from each phase to a random spot of earth would be very undefined.Only when measuring phase to true ground you’ll get voltage close to nominal voltage.
Yes, Mike often addresses the issue of NEV (neutral to earth voltage) but is very clear what he is talking about when he does that.I don't know the specific document(s) he is referring to, but based on the explanation in OP I am picturing an illustration showing a volt meter connected between a grounded and an ungrounded conductor. Good enough for most general topics. If topic of discussion is a stray voltage type of issue or anything else where one may be concerned with the differential in voltage he most likely would include both grounded conductor and earth ground as well as voltage meter readings between them in the illustration, and pretty much has to to give effective explanation of what is going on in those type of situations
But Mike's examples in his publications are not NEC, they are his opinion on how to describe, illustrate, etc. whatever topic he is trying to address.Yes, Mike often addresses the issue of NEV (neutral to earth voltage) but is very clear what he is talking about when he does that.
Anytime you are talking about "voltage to ground" in the context of the NEC, you have no choice but to take that measurement as specified in the Article 100 definition.