So 1/2 emt currently has 3-12 for another circuit one of them is the EGC. I need to run number 6 about 175 to compensate for VD for a RV recep.
I was going to pull the EGC out and use for pull string and just pull two number 6 and just use conduit as EGC.
For VD I know you got to increase EGC (wire) the same you do the phase condutors, Conduit good no matter what correct regardless of VD. I know the EMT is better at clearing a fault then the wire. VD increase just has me guessing I don't see a no in the book