choogenboom
- Beaufort SC
- Electrical Engineer
Can anyone help me reconcile these two quotes:
"Conduit (RMC, IMC or EMT) is an NEC-accepted ground path. So, if the wires are in steel conduit, no OTHER ground wire is required."
"Sealing Locknuts-Sealing locknuts are intended for use with rigid metal conduit and intermediate metal conduit with one sealing locknut in the outside or the inside and either an ordinary locknut or a sealing locknut on the opposite side of the enclosure for wet locations or liquid-tight applications."
Seems like one of them must have a qualifier to the effect of "unless it must be liquid tight" or "unless its relied on for conductivity". And seems like _both_ should have a requirement to verify they work as required. Ie "must test for the conduit to be a working low impedance electrical connection" and "must do a bubble test or similar to confirm a connection is liquid tight.". Or is there no need to test that required things actually work and which case why bother requiring them?
