quincyg
- California
- General contractor
I am working on a 3 unit building with 3 meters. 100A disconnect at meter for main house, 60A disc at meter for Laundry, 70A disc for unit B.
I'm sorting out circuits and loads for the building and discovered that there is a 3 wire tap before the main house 100A panel that feeds the main lugs for Unit A. The 100A wire is an old 2/3 NM(not B) which carries on past the tap near the meter to the main house panel. That other leg of the tap continues to unit A panel lugs. This wire is smaller, but I haven't sized it yet. It's either 3/3 NM or 4/3 NM. All panels are 125A rated panels.
1)I would like to bring this situation up to current code and best practices. My understanding is that having two panels controlled by a single overcurrent protection is not allowed. Not sure of code.
2)2/3 NM is rated at 60 degrees = 95A. 100 ft run. Not sure is 85% rule applies here and don't want to argue it. So this wire is undersized for 100A.
3)The 2/3 NM in photo appears to show signs of overheating in this photo. I can't tell if that is a manufacturing difference where the strands are visible through sheathing or if the wire is stressed. I also see some drip on the bottom of wire, which could be sheathing melt or gel from the tap. The wires have the same look where they land at the panel lugs 100ft away. Anyone seen wires with this look due to overheating?
I likely will want to run a new 100A home run from disconnect to house panel and a new 60A run to unit A. There's currently just a laundry panel on unit A meter that I would feed from the main house 100A panel.
Yes, Load calcs are being done!
Thanks for any advice.