Installer
- DesMoines, Washington
I stopped doing electrical design for 15 years and I’m rusty. I’ve been asked to add a small critical panel in a Building to supply some computer network equipment in a Telco Room. I’m calling this Panel B. I’ve seen this called a Subpanel.
The closest upstream 3 phase panel is a 120/ 208 VAC 100A MLO 42 circuit breaker panel 170’ away in the same Building. I’m calling this Panel A. This panel is lightly used and has 8 KVA of load on it spread against all 3 phases equally and 10 spares.
In my design for the new panel B, I did the following and I respectfully request your feedback as to whether I am doing these things correctly.
- I used a 3 phase 100A panel for Panel B even though a single phase panel was sufficient. This is for future considerations and unanticipated technology changes.
- I installed a Main Breaker on Panel B since its 170’ away from Panel A and there are Security Doors restricting access.
- I derated the new 100A Panel B to 60A by installing a 3 pole 60 Amp Main Breaker at Panel B and using a 3 pole 60 A breaker to feed Panel A. I did this to protect Panel A should it ever have more loads put on it.
- I carried the Ground from Panel A to Panel B as an Equipment Ground and bonded it to the enclosure.
- I installed a TVSS at Panel B. Panel A has a TVSS. What guidelines apply here? What is the NEC guidance in this situation? Do the TVSS’s have to be coordinated or is installing a second TVSS incorrect ?View attachment FENSPNLDesign 9-28.png