I am embarrassed that I have probably installed supplementary protection breakers where I should not have. Been reading up on it and think I have it sorted out. Let me ask a few simple, direct questions to see if I got it right.
Scenario : A single pole 30 amp OCPD MCB is installed to provide protection to a branch circuit with #10 awg wire. Among a number of devices fed by this branch circuit, a 120VAC/24VDC power supply is fed by a 20A supplementary breaker.
Question 1: Does the wire from the supplementary breaker to the PS have to be #10 awg, because #12 awg wire would not be protected? I think this is TRUE.
Question 2: Would feeding another supplemental breaker, 15 amp, downstream of the 20 amp supplementary breaker to provide power to a panel heater, not be allowed even if #10 awg wire were used because this would make the 20 amp supplementary breaker a branch OCPD, which is not allowed? I think this is TRUE.
Scenario : A single pole 30 amp OCPD MCB is installed to provide protection to a branch circuit with #10 awg wire. Among a number of devices fed by this branch circuit, a 120VAC/24VDC power supply is fed by a 20A supplementary breaker.
Question 1: Does the wire from the supplementary breaker to the PS have to be #10 awg, because #12 awg wire would not be protected? I think this is TRUE.
Question 2: Would feeding another supplemental breaker, 15 amp, downstream of the 20 amp supplementary breaker to provide power to a panel heater, not be allowed even if #10 awg wire were used because this would make the 20 amp supplementary breaker a branch OCPD, which is not allowed? I think this is TRUE.