paullmullen
- Wisconsin
- Electrical Engineer & Master Electrician
For reference, here is the text of 220.56 (NEC2017):
Two questions:
1) When calculating the load before the demand factor, do we just add up the demands on the rating plates of the equipment? I can imagine all sorts of more complex approaches including:
- Using T220.55 to calculate the loads.
- Doing load calculations for single phase appliances on three-phase 4-wire systems (Divide loads by 3 and then double)
- and more.
2) When using 220.55's reference to household appliances in instructional programs. What differentiates a household appliance from a commercial appliance?
220.56 Kitchen Equipment — Other Than Dwelling Unit(s). It shall be permissible to calculate the load for commercial electric cooking equipment, dishwasher booster eaters, water heaters, and other kitchen equipment in accordance with Table 220.56. These demand factors shall be applied to all equipment that has either thermostatic control or intermittent use as kitchen equipment. These demand factors shall not apply to space-heating, ventilating, or air-conditioning equipment. However, in no case shall the feeder or service calculated load be less than the sum of the largest two kitchen equipment loads.Two questions: