RustyShackleford
Senior Member
- Location
- NC
- Occupation
- electrical engineer
I mentioned above that there's already 6 AWG NM-B going to the location. I should've stressed that I'm working the problem from the other end. So I'm trying to spec which combination of compressors and heat strips can be supported (without pulling heavier wire). It still comes down to this: which of the many amperage figures quoted for heat pump compressors is the one that should be considered a continuous load; I'm coming to the conclusion that it's MCA (minimum circuit ampacity) with the 125% already baked in (so take 80% of MCA as continuous).The first step is to do a "Heat Load" study, so you know what size of unit you will need.
How can you determine the feeder size if you don't know what size unit you need ?