I am trying to better understand:
This is all normal except that the GEC from the ground rod (next to utility meter and exterior MSP) goes into basement along joists to the ground bar in the primary subpanel. The primary subpanel has grounds and neutrals separated. The copper GEC, coming from ground rod, connects at the bottom of the ground bar. At the top of the ground bar there is an Aluminum ground that goes back to the MSP. So the GEC is not continuous from the GE to the MSP where the N-G connection happens. (unless 250.64(C) applies?)
I don't know why the GEC doesn't just go from ground rod directly to MSP. I would think this would be a violation?
I see an inspection sticker on the primary subpanel, but not the MSP. Maybe inspector only looked in the basement.
I have a residential job with an existing 200A main service panel that has a 200A main breaker. Currently there are no load breakers in this panel, but I am wanting to use 2 spaces of the 8 spaced MSP. There is a neutral wire, L1, and L2 going from the utility meter to the adjacent exterior MSP. L1, L2, neutral and a "ground" going from exterior MSP to a primary subpanel located electrically 15' away in basement. The neutral to "ground" connection happens in the MSP.NEC 2017 250.64(C)(2): Sections of busbars shall be permitted to be connected
together to form a grounding electrode conductor.
This is all normal except that the GEC from the ground rod (next to utility meter and exterior MSP) goes into basement along joists to the ground bar in the primary subpanel. The primary subpanel has grounds and neutrals separated. The copper GEC, coming from ground rod, connects at the bottom of the ground bar. At the top of the ground bar there is an Aluminum ground that goes back to the MSP. So the GEC is not continuous from the GE to the MSP where the N-G connection happens. (unless 250.64(C) applies?)
I don't know why the GEC doesn't just go from ground rod directly to MSP. I would think this would be a violation?
I see an inspection sticker on the primary subpanel, but not the MSP. Maybe inspector only looked in the basement.