We have an existing building that if supplied by a 3 phase service. Someone put a single phase panel in, where there is a 3phase 4 wire feeder, 120/208. Is there any reason we cannot leave it the way it is, with one leg capped off?
Then if the 4th conductor is unconnected at both ends, it's a spare conductor, and the Note to Table 310.15(C)(1) says that spare conductors are counted as current carrying conductors. So that means you have 4 current carrying conductors and would need to apply a 80% adjustment factor.In this case the neutral wire becomes a current carrying conductor.
Which could be a problem for the ampacity, although it in this case a problem easily side stepped by just energizing the conductor at the supply end with the third phase. An odd outcome of the way the rules are written.
Cheers, Wayne
If the conductor is energized by the third phase at the supply then (a) I would no longer call it spare, even if it has no load and (b) you definitely have a 4-wire 3 phase feeder, which is definitely only 3 CCCs (assuming no majority of non-linear loads).How does terminating the conductor at the supply end and capping off the load end versus not terminating the conductor at either end change the definition of a spare conductor?
Cheers, Wayne
maybe I will have them phase it to green and make it a full size EGC.Then if the 4th conductor is unconnected at both ends, it's a spare conductor, and the Note to Table 310.15(C)(1) says that spare conductors are counted as current carrying conductors. So that means you have 4 current carrying conductors and would need to apply a 80% adjustment factor.
Cheers, Wayne
You raise a good point. But all 310.12(E) cares about is whether the neutral can only carry the unbalanced current from the ungrounded conductor. By energizing the spare conductor with the 3rd phase, you ensure that is true, so the neutral doesn't count. Even if the formerly spare conductor has no load on it.How would you have a 3ph 4 wire feeder if one of the phase conductors is capped off on the load end and not terminated ?
Only if you energize the spare with the 3rd phase. You could in theory energize it with, say L1, and then you'd have 4 CCCs, maybe 2 circuits, one L1-N and one L1-L2. So it's not so crazy to count the spare. If you energize it now as L3, then there's no issue.But in this case if that spare conductor gets used, the neutral wouldn't be a CCC. So you never have 4 actual CCCs.
I meant that jokingly. I would not make them change it because there is no scenario where there would be 4 CCCsWhy?
JAP>
Cheers, Wayne
Disagree. By energizing it on the line side, you dictate its behavior if any load were applied to it. The fact that no load is applied to it is immaterial.A conductor can't simply be energized on the line side and not landed on the load end to make any difference because it lacks the capability to complete any circuit whatsoever.
Cheers, Wayne
But at same time if and when you ever put it to use it likely turns the neutral back to a non CCC for adjustment purposes. So that makes it 3CCC's in the raceway whether utilizing as single phase 3 wire or utilizing as three phase 4 wire. IMO if that is not what they intended they need to clarify more in the wording.Then if the 4th conductor is unconnected at both ends, it's a spare conductor, and the Note to Table 310.15(C)(1) says that spare conductors are counted as current carrying conductors. So that means you have 4 current carrying conductors and would need to apply a 80% adjustment factor.
Cheers, Wayne
You could extend the conductor to a new enclosure and use it.But there's no possibility of a load being applied to it seeing as how it wouldn't be landed on the load end.
Likely, yes; definite no. But by energizing it on the line side, the uncertainty is gone--if the conductor is used on the load side, there will be only 3 CCCs.But at same time if and when you ever put it to use it likely turns the neutral back to a non CCC for adjustment purposes.