Hi folks!
Had my home built 2 years ago but I just noticed something. I noticed that my 4 ton 5 head mini split system has a #12 yellow gauge wire running to it with a 20 amp breaker at the circuit panel. I've never had any trips or issues even with all the units running full in the winter. But from reading through the forum I'm not sure if this will apply to that rule for sizing 440 NEC. Regardless since I haven't had any issues is this an issue due to code or fire hazard? Is #12 sufficient enough and safe? Or do I need something like #10 to replace it?
The specs on my mini split system:
MODEL DAIKIN 5MXS48TVJU
POWER SUPPLY: SINGLE PHASE 208/230V 60Hz
MAXIMUM OVERCURRENT PROTECTIVE DEVICE: 35 A
MINIMUM CIRCUIT AMPACITY: 33.2 A
Had my home built 2 years ago but I just noticed something. I noticed that my 4 ton 5 head mini split system has a #12 yellow gauge wire running to it with a 20 amp breaker at the circuit panel. I've never had any trips or issues even with all the units running full in the winter. But from reading through the forum I'm not sure if this will apply to that rule for sizing 440 NEC. Regardless since I haven't had any issues is this an issue due to code or fire hazard? Is #12 sufficient enough and safe? Or do I need something like #10 to replace it?
The specs on my mini split system:
MODEL DAIKIN 5MXS48TVJU
POWER SUPPLY: SINGLE PHASE 208/230V 60Hz
MAXIMUM OVERCURRENT PROTECTIVE DEVICE: 35 A
MINIMUM CIRCUIT AMPACITY: 33.2 A