Jimmy7
- Boston, MA
- Electrician
Yes that is strange given that the generator is only 45 kw. Also there should not be a #3 EGC from the pole to the meter main.I knew about the service size and the load the generator will serve, but the 400 AMP breaker at the generator was confusing me. I appreciate the feedback.
I agree... Thank you!Yes that is strange given that the generator is only 45 kw. Also there should not be a #3 EGC from the pole to the meter main.
YW.I knew about the service size and the load the generator will serve, but the 400 AMP breaker at the generator was confusing me. I appreciate the feedback.
Is the generator 120V?YW.
It should be 200a. A 200a 240v service is 48kw.
It's indicated to be "120/240v 1ph 3W"Is the generator 120V?
So is the ATS.It's indicated to be "120/240v 1ph 3W"
For residential, offices, retail or similar yes. For industrial or industrial like applications depends on load served. A lot of the agriculture loads I deal with may be seasonal to some extent but when they are loaded they are loaded and for many hours at a time. Grain handling I have yet to see a standby generator or at least one that is intended to run the entire facility if needed. Livestock operations however can have a need to handle entire facility with a standby generator, and many them are not your grandparents farm anymore they are like mini industrial plants some even with 600 + amp 480/277 volt three phase services when it comes to electrical service and distribution.That's probably an appropriately sized generator for a 400 amp service from an actual realistic standpoint, although NEC calcs may show otherwise.