I have a solar installation here in northern Illinois that the solar installer wants to connect 1000A onto a 1600A bus in a switchgear with no main breaker. The gear already has 2000A of load with three breakers (800, 600, 600) on the bus.
His response to my concern is as follows:
At this particular site, we do not have a single main breaker, and we are using the 6 disconnecting means rule. The interconnection is line side of the existing disconnecting means/devices and would be interconnected under 705.12(A), allowing per 230.82(6) to be interconnected line side, and that the sum of all “Power Production Sources” (i.e. solar) do not exceed the rating of the service. In our case, this is 1000A of Solar compared to the 1600A service.
References:
705.12(A) Supply Side. An electric power production source shall be permitted to be connected to the supply side of the service disconnecting means as permitted in 230.82(6). The sum of the ratings of all overcurrent devices connected to power production sources shall not exceed the rating of the service.
230.82(6) – Solar photovoltaic systems, fuel cell systems, wind electric systems, energy storage systems, or interconnected electric power production sources
This seems like a violation to me because there is no single service disconnecting means to protect the bus.
I welcome any comments and am always open to learning!
Thanks, Lori
His response to my concern is as follows:
At this particular site, we do not have a single main breaker, and we are using the 6 disconnecting means rule. The interconnection is line side of the existing disconnecting means/devices and would be interconnected under 705.12(A), allowing per 230.82(6) to be interconnected line side, and that the sum of all “Power Production Sources” (i.e. solar) do not exceed the rating of the service. In our case, this is 1000A of Solar compared to the 1600A service.
References:
705.12(A) Supply Side. An electric power production source shall be permitted to be connected to the supply side of the service disconnecting means as permitted in 230.82(6). The sum of the ratings of all overcurrent devices connected to power production sources shall not exceed the rating of the service.
230.82(6) – Solar photovoltaic systems, fuel cell systems, wind electric systems, energy storage systems, or interconnected electric power production sources
This seems like a violation to me because there is no single service disconnecting means to protect the bus.
I welcome any comments and am always open to learning!
Thanks, Lori