I am a licensed electrical contractor 25 yrs in buisiness. I have an inspector who is telling me that when I have 3 wires together immediately after exiting fire stopped hole that i have to derate the wire again(compounding the deration) of where i came through the hole. So 334.80 says I derate the wires in the hole, I have 6 # 14 conductors (3 -14-2 romex) so going to 310.15(c)(1) 4-6 conductors gets derated to 80%
now going from 90% column of 310.16 ................ 14awg is rated 25 amps
so derating the wires in the hole would be ......... 25amps X .8= 20 amps (wire is rated for 20 amps after derating, going on a 15 amp breaker)
Now he says since the 3 wires in the hole are stacked together immediately after exiting hole for longer than 24" I have to further derate from the derated ampacity from the hole. So i guess he thinks i dont follow what the code says and derate the sections in question on their own. That I would instead derate the hole and take that number to further derate for the wires stapled down the stud to the switch. (2 wires under staple 3rd wire wire tied to other two)
So he is saying ................................................................................Hole derated to 20 amps
derate 3 wires together from already derated wire 20amps x .8=16 amps (while this is still over the 15 amps that is not the point, if one of those wires was a 3 wire and I had to go to 7-9 conductors @70% I would be over) Yes I know I can use stackers but not the point because where does it end. Selection of ampacity 310.14(a)(2) says there can be more than one ampacity for a given length of wire and you use the lowest. Please tell me if I am wrong. BTW the code handbook has a perfect example of 4 12- 2 romex without airspace and their conclusion says you can have romex wires (no more than 9 conductors) without airspace in almost all circumstances without having to upsize the wire due to derating. My understanding is you derate the hole... 25 amps X .8 %=20amps
Then you derate the 3 wires together ..........25 amps X .8%=20amps