The code allows terminating onto a larger breaker than what the wire is rated for as long as it is protected at its origin by a breaker sized to its ampacity.Yes
I understood all this but my concern was regarding if code would allow terminating onto a larger breaker (but not whether it would cause excessive current and heat for conductor) than conductor 60 to 75 degree terminating ampacity. Code can always overrule something that works and not allow it just because it’s a code.
That is not your problem. Your problem is using a wire that is not an approved wiring method.