electrician09
- United States
- Electrician
I understand according to article 334.112 NM-B conductor insulation shall be rated 90c , but the ampacity must be sized according to the 60c Column. And only use 90 for correction purposes.
However is NM-B allowed to be terminated to a straight 75c breaker or must it only be terminated to a 60/75c breaker?
Example: two pole 30 amp breaker with a 75c only wire rating, allowed to have 10 awg NM-B terminated to it since the conductor insulation is rated for 90c but the cable assembly ampacity must be rated from the 60c column.