If the feeder originates from a separate building do you need to have a disconnect before the 400-amp panel that has a main breaker?
maybe. where is the panel located?If the feeder originates from a separate building do you need to have a disconnect before the 400-amp panel that has a main breaker?
In a new water pump building. The Feeder will stub-up right into the bottom of the panel with maybe a short steel nipplemaybe. where is the panel located?
btw, the panel rating is not relevant.
Yes it is a new building and conduit will have a short steel nipple right into the panel(a) is the 400 amp panel "nearest the point of entry of the conductors"
OR
do you qualify under the exception to 225.32
Then you should be fine.Yes it is a new building and conduit will have a short steel nipple right into the panel