- Connecticut
- Engineer
So any transformer that has primary protection at not greater than 125%, doesn't need transformer secondary protection.Yes I only see the table that shows primary at 125% with no secondary protection
IMHO... That is correct, but if you are installing a panelboard on the secondary of the transformer, then OCPD for the panelboard is required.So any transformer that has primary protection at not greater than 125%, doesn't need transformer secondary protection.
Yes. Secondary conductor protection is also required.IMHO... That is correct, but if you are installing a panelboard on the secondary of the transformer, then OCPD for the panelboard is required.
Or maximum of 250% primary protection if secondary 125%
In most cases the rules in 240.21(C) will require protection for the transformer secondary conductors, or as you said 408.36 will apply.IMHO... That is correct, but if you are installing a panelboard on the secondary of the transformer, then OCPD for the panelboard is required.
Correct.In most cases the rules in 240.21(C) will require protection for the transformer secondary conductors, or as you said 408.36 will apply.
It is just that that the rules in 450 only apply to the protection of the transformer itself.
But the NEC code book says to use the table which says you can protect the primary to 250% ampacity if secondary is protected and system is over 9 amperes.Correct.
You could have a1000A panelboard with a 600A main breaker fed with 800A of conductor on the 208Y/120V secondary of a 75kVA as long as the primary ptotection is not more than 125%. Nothing like provisions for future growth.
You can go all the way up to 250%, Only if you have secondary protection sized at no more than125%. The example I gave does not meet this requirement.But the NEC code book says to use the table which says you can protect the primary to 250% ampacity if secondary is protected and system is over 9 amperes.
Most I see use only 125% on primary OCPD however
It's similar to testing ground rod resistance. Easier to put in two and go home.You can go all the way up to 250%, Only if you have secondary protection sized at no more than125%. The example I gave does not meet this requirement.
Most people do not research the predicted inrush of the transformer and then select the appropriate protective devices. Instead they simple jump to the maximum allowed per their installation.
Except the transformer current can usually be determined with an email before the material is bought and simply oversizing may waste, space, resources, and money.It's similar to testing ground rod resistance. Easier to put in two and go home.
There are almost always exceptions.Except the transformer current can usually be determined with an email before the material is bought and simply oversizing may waste, space, resources, and money.
Isn’t the OCPD for the panel on the secondary also overload protection or OCPD for secondary side and would have to be protected at 125% of secondary current?In most cases the rules in 240.21(C) will require protection for the transformer secondary conductors, or as you said 408.36 will apply.
Oftentimes if the transformer is feeding a single that is the case but not necessarily so.Isn’t the OCPD for the panel on the secondary also overload protection or OCPD for secondary side and would have to be protected at 125% of secondary current?