Dark Sparky
- USA
- Electrical Engineer
I have a facility requiring full-building power backup. It will take a 1200 amp service. Although I will have a full-capacity generator, I would like to avoid needing separate transfer switches (ATS's) for article 700 emergency power vs. article 702 loads. Thus the plan is to have the emergency lights have batteries, and the generator power the rest of the facility's loads (all article 702 loads) in an emergency.
In practice, what is the best way to efficiently "split off" the small amount of normal power for the battery-fed emergency lights? I would like to avoid this obvious approach due to cost: utility power feeds 1200 amp main distribution panel - which splits the power (~1200A to ATS normal power vs. ~100A to the emerg lighting panel) - because downstream of the ATS I would require yet another 1200A MDP - thus a total of (2) 1200A MDP's.
Am I missing an obvious and cost effective solution? (This was a difficult question to nail down a search for in the forums - I can't come up with a search string that narrows down on this question.) Thanks.