ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
I apologize for the rookie question, but residential service design is a bit off my map. Regarding 310.12(A), does this allow 2/0 copper service conductors for a single family dwelling to feed a 200A main breaker in an MDP? It seems to, if the "service rating" means the rating of the service disconnect OCPD rating.