ffroh
- New Jersey
- Electrician
I was hoping someone can help with the calculations. I don't normally install transformers. I am not sure about picking out the correct conductor from table 310.16. What column? Bonding jumper? Grounding electrode conductor?
450.3(B)
75 KVA transformer primary 480 volts, 3 phase and secondary 480 volts 3 PH.
I= VA / (E X 1.732)
75,000 VA / (480 V X 1.732) = 90A
90A X 1.25 = 112.5A
240.6 OCPD = 125A
Primary conductor sizing
90A X 1.25 = 112.5A
# 1 Copper THHN run in EMT.
Secondary conductors
90 X 1.25 = 112.5A
MC Cable Copper # 1
250.102(c)(1) Bonding jumper copper # 6
250.66 Grounding electrode conductor copper # 6
41.5 KVA transformer primary 480 volts, 3 phase and secondary 400Y/231, 3 PH.
I= VA / (E X 1.732)
41,500 VA / (480 V X 1.732) = 50A
50A X 1.25 = 63 A
240.6 OCPD 70A
50A X 1.25 = 63 A
MC Cable Copper THHN # 6
41,500 VA / (231V X 1.732) = 104A
Using MC Cable?
450.3(B)
I= VA / (E X 1.732)
90A X 1.25 = 112.5A
240.6 OCPD = 125A
90A X 1.25 = 112.5A
90 X 1.25 = 112.5A
MC Cable Copper # 1
I= VA / (E X 1.732)
50A X 1.25 = 63 A
240.6 OCPD 70A
50A X 1.25 = 63 A
Using MC Cable?