ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
It seems unlikely to me that a panel would comply with both rules, since in order to comply with the 120% rule the breaker protecting the busbar must be part of the calculation.Not sure which method you're referring to. But something like that only makes sense where a panel would presently comply with both the "120% rule" and the "sum of all breakers rule". Unless you can only use the latter rule, and the sum would exceed the rating, adding a load doesn't matter.