- Chapel Hill, NC
- Retired Electrical Contractor
Based on the 30 degree phase shift as Don described, the law of cosines gives the voltage via this calculation:What is the calculation used to get 381 v.
Why the 30 deg phase shift? Just mfg, or an actual difference created by the transforming to the lower voltage? (Can you get a transformer that doesn't create the phase shift referenced).You have to remember there will be a 30° phase shift between the hots on the 480Y/277 system and the 208Y/120 volt system
It is the construction of the transformer and I think all delta/wye have the same 30° shift.Why the 30 deg phase shift? Just mfg, or an actual difference created by the transforming to the lower voltage? (Can you get a transformer that doesn't create the phase shift referenced).
With the 30 deg shift would you be able to simply meter between the 2 separately derived systems?
What issues (if any) would arise from even attempting to meter between the 2?
That doesn't really work...you have to do vector addition...see post #7.A 277V circuit is the neutral voltage of a 480V, 3-phase system while the 120V circuit is the neutral voltage of a 208V, 3-phase system. The utilization voltages of 480 and 208V systems are 460V and 200V respectively. Therefore, 460/1.732 + 200/1.732 = 265.58V + 115.47 ~ 381V. Crystal!
In the diagram in post #7, if the 208Y/120V is created by a transformer with a 480V delta primary, then its primary side coils will be connected between the tips of the yellow, orange, and light brown vectors. The triangle defined by those tips isn't drawn in, but you can see that the blue, red, and black vectors are parallel to sides of that triangle. Which is what the transformer does, it creates a voltage on the secondary coil in phase with the voltage on the primary coil.Why the 30 deg phase shift?
I See the illustration post #7, makes sense. Your description sounds as if indicating a Delta grounded primary.In the diagram in post #7, if the 208Y/120V is created by a transformer with a 480V delta primary, then its primary side coils will be connected between the tips of the yellow, orange, and light brown vectors. The triangle defined by those tips isn't drawn in, but you can see that the blue, red, and black vectors are parallel to sides of that triangle. Which is what the transformer does, it creates a voltage on the secondary coil in phase with the voltage on the primary coil.
So the phase shift is the same phase shift you see on the primary side between L-L and L-N. Since the transformer is using the primary L-L to generate the secondary L-N, the secondary L-N is in phase with the primary L-L, rather than the primary L-N.
Cheers, Wayne
P.S. The arithmetic in post #4 is shown in post #7 as the brown vector plus the blue vector (actually the difference).
Yes, the assumption is one of the two wye systems is derived from the other via a delta-wye transformer, as is typical.I See the illustration post #7, makes sense. Your description sounds as if indicating a Delta grounded primary.
sqrt(1202 + 2772 + 2*120*127*cosine(30 degrees)) = 386V
Cheers, Wayne
If separately derived systems have a common primary, can that Phase-Rotation meter find distribution voltage potential that blows up in your face?What issues (if any) would arise from even attempting to meter between the 2?
I miss him.
With all the neutral effectively grounded, there must be a common reference point. Why take the complicated way when the simplest explanation is the best one? Occam's Razor tells me that should be the way, or isn't it? ("The best explanation of any phenomenon is the one that makes the fewest assumptions.")That doesn't really work...you have to do vector addition...see post #7.
It is the easiest, but the values require vector addition.With all the neutral effectively grounded, there must be a common reference point. Why take the complicated way when the simplest explanation is the best one? Occam's Razor tells me that should be the way, or isn't it? ("The best explanation of any phenomenon is the one that makes the fewest assumptions.")