Alwayslearningelec
- NJ
- Estimator
MOCP??? Motor overcurrent protective device?If the MOCP is less than the ckt amps - like maybe 10 or 15 on this 20A ckt
- then a fused disc could be used.
Maximum Overcurrent Protective Device. Info on the AC equipment nameplate.MOCP??? Motor overcurrent protective device?
This is a disputed concept, and quite in depth. I bet someone here can point you to some of the discussion here. But OP, he means when the SCCR (short circuit current rating) of the equipment is below the fault current calculated to be available at the unit, then you use fuses to reduce the available fault current. Again, some people come down that it is acceptable, others state only when the entire assemble is tested and listed for that reduction.It's the fault current environment that determines when a disconnect must be fused. Unfused disconnects have a short-circuit rating of 10kA, unless rated with the breaker or fuse that feeds it.
I was involved in a design 15 years ago where the drywall manufacturing facility had around 100 disconnects for motors. Value engineering said replace any of the fused disconnects with unfused, and for that facility I think we ended up only replacing around 1/3 or 33 units, which is to say that the need for fused disconnects (>10kA) is more likely.
Yeah, more specifically when the nameplates states, MOCP then you can use a breaker. Other nomenclature is often, Max fuse, or Max fuse or breaker, and I have seen unites that actually list different values for max fuse vs. max breaker.In addition to the above:
Some equipment calls for "fuse protection only" in which case there must be fuses in the supply.
We often used fusible as the units turned out to have different values that expected it was easier to find odd size fuses than breakers.