I don't see how a "dedicated neutral conductor" can be anything but a neutral for every circuit meaning no MWBC's. Not the best choice of words but the meaning is there. If MWBC's were permitted then the wording would not be needed.
A couple thoughts:
1) It could be to nix any thoughts of using a common neutral for multiple circuits, like jpflex is raising (I think). The NEC prohibits that for branch circuits, but not feeders. Plus some newbs don't understand it.
2) It could require a neutral to be pulled with all circuits even if they only have L-L loads.
I'll stick with "you're probably right but I'm not 100% sure". It moght be clearer in context.