Good morning,
I am having an issue with the "Building Official" at City of Westlake.
I have an irrigation timeclock only (no pump) for which we have a standalone service rack. #6 cu for the service lateral and feeders, 60 amp main. The load can't be more than 2-3amps. The rack is 400 feet from the transformer and the inspector/building official is claiming I need to provide a voltage drop calculation and the amperage figured in the calculation needs to be the 60-amp service rating, not the actual load.
I explained to him my understanding that voltage drop calculations are not a code requirement, but rather a recommendation, primarily for the engineer (if distance is known) and/or the contractor (if distance is determined in the field), for appliance performance/efficiency. Secondly, the voltage drop applies only to feeders and branch circuits, not service laterals. Lastly, the connected load is the amperage used in the calculation, not the service rating.
Is it me or is this guy off his rocker? I am being forced to run 400' of 2/O copper in 2" pvc for a 2-3 amp irrigation timer (sitting in a 4 ckt N3R panel)...