I guess sometimes you learn some things the hard way. With that being said, if I wanted to make this right, what is the easiest way out of this? I do have the two 2 1/2 stubbed in with male adapters on them already. Would I just throw some steel coupling on them and run some flex with three 3/0 and #4 ground ( I don’t think I would need the 1/0 like what was in the ser cable for 200 amps).
 

Attachments

  • IMG_1469.jpeg
    IMG_1469.jpeg
    20.1 KB · Views: 4
With that being said, if I wanted to make this right, what is the easiest way out of this?
I would run the conduits continuously to where the panels go, and then attach them where the conduits end. That's easier than fitting the conduits to the panels. You don't have to use the center knockouts.
 