Terminals 95 and 96, the NC contact, are used on all IEC overload relays to open the power to the contactor coil.This may be due to the difference between normal contact position when de-energized and when in use.
I'm not seeing what you see. Can you help meAnd this here might confuse it more. See if you can find where it is self-contradictory: https://studylib.net/doc/18040687/nema-and-iec-terminal-markings
Top left is a table explaining the numbering system (Sure would like to see a complete, official one.) Bottom left is a diagram showing the contacts in a schematic. The table says 95 & 96 are NO, the diagram shows 95 & 96 as NC.I'm not seeing what you see. Can you help me
Thanks, I will review again.Top left is a table explaining the numbering system (Sure would like to see a complete, official one.) Bottom left is a diagram showing the contacts in a schematic. The table says 95 & 96 are NO, the diagram shows 95 & 96 as NC.
I used to do electrical design at a manufacturing plant and I notice stuff like that. Sooooo nice to be back in the field, even with a boss that is, er, simple-minded.
Gosh, sorry, I am trying to understand what you are asking. I enjoy a good conversation about electrical documentation. "I have used these for singling" Don't know what you mean. Can you give an example?I enjoy learning new things.
I reviewed the table.
Could you give me an example how this would be applicable. I have used these for singling. Never for anything else.
I'm also aware these numbers can be used elsewhere other than the over load block N.O.
For other control items based on the symbols in table.
I would not think in this case it's applicable for the OP question. However I'm willing to learn.
Thank you in advance.
That's a quirk of the concept of "normal". In IEC world, the 95/96 contacts are in fact "normally" open, held closed by a spring loaded mechanism tied to the OL thermal element. If the thermal element releases the trip bar, the contacts RETURN to their "normal" state of being open.Top left is a table explaining the numbering system (Sure would like to see a complete, official one.) Bottom left is a diagram showing the contacts in a schematic. The table says 95 & 96 are NO, the diagram shows 95 & 96 as NC.
I used to do electrical design at a manufacturing plant and I notice stuff like that. Sooooo nice to be back in the field, even with a boss that is, er, simple-minded.
That does not explain why the table says one thing and the diagram shows another.That's a quirk of the concept of "normal". In IEC world, the 95/96 contacts are in fact "normally" open, held closed by a spring loaded mechanism tied to the OL thermal element. If the thermal element releases the trip bar, the contacts RETURN to their "normal" state of being open.
.....
I looked. It's Sunday so I'm not supposed to do anything, but still it's frustrating to look and look and look without finding it, so I'm posting what I found so far, then I'm giving up.Still would LOOOVE to see a table of the terminal numbers.