I still get confused at times on how to treat OCPD when planning the complete circuit from source 3 phase panel to the motor load
What I have figured out so far is:
1) CONDUCTORS Branch circuit wires to motor feed = 4 AWG THHN at 75 degree termination
2) OCPD = 175 I inverse breaker (for branch circuit feed)
65 FLC x 250% max = 162.5 i amperes go to next standard size up = 175 ampere breaker
3) GEC = # 6 AWG based on upstream 175 ampere breaker
4) EMT 1/1/2 inch size based on 3 x #4 AWG THHN plus 1 # 6 AWG equipment ground conductor
However, I am aware that under certain conditions such as in dwellings (which this is not being installed in) must be broken or supply power must be divided when the load is over 60 ampere or more
I am not sure if this NEC rule affects my set up in an industrial setting or how to go about doing this? Do I get a three phase panel with 3 individual breakers for each phase rated for 175 amperes, 1 three phase breaker with 3 ties, or do I assume each phase is 1/3 of the total 175 amperes and thereby get three 60 ampere breakers for each phase?
What I have figured out so far is:
1) CONDUCTORS Branch circuit wires to motor feed = 4 AWG THHN at 75 degree termination
2) OCPD = 175 I inverse breaker (for branch circuit feed)
65 FLC x 250% max = 162.5 i amperes go to next standard size up = 175 ampere breaker
3) GEC = # 6 AWG based on upstream 175 ampere breaker
4) EMT 1/1/2 inch size based on 3 x #4 AWG THHN plus 1 # 6 AWG equipment ground conductor
However, I am aware that under certain conditions such as in dwellings (which this is not being installed in) must be broken or supply power must be divided when the load is over 60 ampere or more
I am not sure if this NEC rule affects my set up in an industrial setting or how to go about doing this? Do I get a three phase panel with 3 individual breakers for each phase rated for 175 amperes, 1 three phase breaker with 3 ties, or do I assume each phase is 1/3 of the total 175 amperes and thereby get three 60 ampere breakers for each phase?