jaylectricity
- Massachusetts
- licensed journeyman electrician
It’s always been orange and b phase in the panel for as long as I can remember. (At least since the late 70’s) The reason it is required on B phase at the service disconnect, is it’s always the center phase, especially in a switchgear, if it is accessible from the back. I take it though some jurisdictions had their own way of identifying and location. Most that land on “C” in the service disconnect, is because the electrician didn’t know the code requirement.Long ago, did the NEC specify the high leg on the first phase instead of the middle? And red instead of orange? I think I recall seeing a very old installation that was done that way. So back then, the meter base would have somewhat matched the service construction, high leg on one side.
Re: the 10k breaker - it seems common for Siemens to provide big main breakers with a such a small SCCR, more common than the other manufacturers. I think they all have their high-end products and low-end, but I've used new residential service equipment from all 4 of the biggest manufacturers, and it seems easier to get a higher SCCR on the main breaker with the other three brands.
Not that I remember, and yes. It was red, but it was always in the middle as far as I recall.Long ago, did the NEC specify the high leg on the first phase instead of the middle? And red instead of orange?
Not always. It was even called the red phase. Some panels had red coloring along the bus.It’s always been orange and b phase in the panel for as long as I can remember. (At least since the late 70’s)
I think it may have come from utilities marking it red on their end, so electricians just followed suite. The code classes I took at trade school, it was orange and “B” phase then. I think we were studying the 78? Code book.Not that I remember, and yes. It was red, but it was always in the middle as far as I recall.
I've been doing electrical work for well over 50 years, and seen and worked on much older than that.I think it may have come from utilities marking it red on their end, so electricians just followed suite. The code classes I took at trade school, it was orange and “B” phase then. I think we were studying the 78? Code book.
I just know it’s been orange by code since the 80’s. Anything past that would be local jurisdiction requirements.I've been doing electrical work for well over 50 years, and seen and worked on much older than that.
Oh, I acknowledge that I'm talking about much older installations. I didn't intend to contradict anyone.I just know it’s been orange by code since the 80’s. Anything past that would be local jurisdiction requirements.
I’m just saying that might be where the red and placement came from in the earlier years.Oh, I acknowledge that I'm talking about much older installations. I didn't intend to contradict anyone.