Main Breaker kAIC Rating Justification
JimmysLimeade
EE Student & PV Design
Utah
PV Design
Miami Gardens is now requesting these calculations to justify the kAIC rating of a new MB when doing any service upgrade. I have made calculations according to a letter from FPL that has the available fault current at the transformer and went from there.
Do these look okay? If I get a number below 10kA, can I say that a 10kAIC rated main breaker is the minimum required and that a larger rated main breaker can be installed (like a 22kAIC rated MB)?
This seems like overkill by Miami Gardens but they require it so I have to provide it...
I am a 3rd party designer for solar installers. One of my clients is requesting that we make these letters. I dont do this for any other AHJ because I dont deal with any permitting, and leave that up to the electrician to decide on the rating of the main breaker when it is needed. I just want to make sure I did this correctly before sending it to my client
Using Bussmann;s FC² I come up with a different number but it's still less than 10k,
Do you have a picture? I might be missing something in my calculations
I went through Bussman FC2 (hopefully I did it correctly) and came up with this:1707855667533.png
Should I be going off of the L-N ISC? My calculated L-L was 8934A which seems like a rounding error on my end compared to the 8935A calculated here.