We'd be glad to help, but we'd like to see your participation. Please share your work so far, and we'll offer feedback to help you the rest of the way.What’s the voltage drop of 125 ft. of 12 AWG wire (0.24 ohms) on a balance 3-wire, 120/240V multiwire circuit supplying a 16A load?
Why the voltage drop answer form the Mike Holt's book is 6.70V dropped on phase wire.
Step 1: Evd = I x R.We'd be glad to help, but we'd like to see your participation. Please share your work so far, and we'll offer feedback to help you the rest of the way.
You're correct up to Step 6, as long as you notice that you used the 1-way length of the circuit. So 16A x 0.24 Ω is the voltage drop on just one of the #12 conductors of the circuit. But current will be returning on the other line of the circuit (no current on the neutral as it is described as a balanced circuit), so that #12 conductor will also have voltage drop.Step 6 : Evd = 16A x 0.24 Ω
Step 7 : Evd = 6.70V dropped on phase wire ?
Step 7 is from Mike Holt's book:You're correct up to Step 6, as long as you notice that you used the 1-way length of the circuit. So 16A x 0.24 Ω is the voltage drop on just one of the #12 conductors of the circuit. But current will be returning on the other line of the circuit (no current on the neutral as it is described as a balanced circuit), so that #12 conductor will also have voltage drop.
That makes the total voltage drop 2 x 16A x 0.24 Ω.
Cheers, Wayne
Step 7 is from Mike Holt's book:Look at the question closely
I come up with 6.68552
Hmm, 2 * 16A * 0.24 = 7.68V, which is not 6.7V.Step 7 is from Mike Holt's book:
6.70V.
How you come out with this number?Look at the question closely
Are these your steps or what is in the book?Step 1: Evd = I x R.
Step 2 : I =16A.
Step 3 : R = (1.93 Ω per 1,000ft/1,000) x 125 ft x 1 wire. [1.93 Ω – 12 AWG from Table 8, Chapter 9]
Step 4 : R = 0.00193 Ω x 125 ft x 1 wire
Step 5 : R = 0.24125 Ω ≈ 0.24 Ω
100% from the book
There is some way to send this question back to him?If these were the steps in The book.
The ansawer has to be wrong and my equation and idea how to solve is incorrect.
16*.24 = 3.84.
This may be one of those that has to sent to Mike holt for the correct answer.
Sorry for any confusion.