Jpflex
Electrician big leagues
- Victorville
- Electrician commercial and residential
I was wandering if you would include the control circuits for motor starters as current carrying conductors within the same conduit containing power and lighting circuits. I’ve seen some starter magnet contacts carry as much as 1-2 amperes per starter with paralleled connections having as much current as lighting circuits.
There was one time I found the inductance in Henry’s of a starter contact coil mathematically by measuring the starter contact current
When determining which conductors to count as current carrying within a conduit for ampacity correction, my book says you would not include control and signal conductors that generally will carry small amounts of current (same as lighting circuits - but lighting circuits are counted?) and these circuits on for only a short period of time (not true for starter control circuits which hold contacts closed as long as the motor runs).
Since control wires for motors are in continuously as the motor runs and can indeed draw adequate current equal to power and lighting circuits within 20 amperes (several motor starter signal circuits all paralleled from 1 branch circuit) shouldn’t they be counted as current carrying conductors when determining conductor corrected ampacity?