wwhitney
- Berkeley, CA
- Retired
Oops, that's not the IRC chart (I was thinking of R702.7(3) on when you can use a Class III vapor retarder), but that is the correct approach for actually determining the temperature of the interior face of the sheathing.The IRC has a chart in it that tells you the minimum ratio of exterior continuous R-value to wall cavity R-value based on climate zone, and it's precisely for this purpose.
If you have Ro insulation outside the sheathing, and Ri insulation inside the sheathing, and To is the outside temperature, Ti the inside temperature, then the approximate sheathing temperature is (Ti*Ro + To*Ri)/(Ro + Ri).
Cheers, Wayne