Flexible 500 KCMIL 1/C 600v cable ?

Status
Not open for further replies.

Dale001289

Senior Member
Location
Georgia
I have a short run of about 12’ but I need extremely flexible cable for tight bend radius inside the junction box
What’s the best option for this application?


Sent from my iPhone using Tapatalk
 
Take a look at cobra x-flex its listed as THW probably has a better bend radius than dlo and is likely smaller OD.
 
Just don't try to use the manufacturer's published ampacities, because, in most cases, they are in free air and at 90°C....and it is unlikely you can use that ampacity for your installation.
 
Because of the nonstandard circular mil area of DLO, you cannot find DLO ampacities in the ampacity tables. A couple of cycles ago this was added to 310.15 to address that issue.
Under engineering supervision, ampacities of sizes not shown in ampacity tables for conductors meeting the general wiring requirements shall be permitted to be determined by interpolation of the adjacent conductors based on the conductor’s area.
 
I have a short run of about 12’ but I need extremely flexible cable for tight bend radius inside the junction box
What’s the best option for this application?


Sent from my iPhone using Tapatalk
What about type G-GC cable? I have used that on projects where the machinery moves. It's way more flexible that THHN.
 
Because of the nonstandard circular mil area of DLO, you cannot find DLO ampacities in the ampacity tables. A couple of cycles ago this was added to 310.15 to address that issue.
What they should have done is allow linear interpolation without engineering supervision, and non linear interpolation with engineering supervision.
 
What they should have done is allow linear interpolation without engineering supervision, and non linear interpolation with engineering supervision.
The problem with that is, the capacity of conductors per cmil decreases more than linearly as you go up in size, due to the center having to dissipate all the way through to the edges. One reason parallels are more economical.

Maybe they should just include the capacity of the common DLO sizes, 444, 535 etc in the tables somehow.
 
What about type G-GC cable? I have used that on projects where the machinery moves. It's way more flexible that THHN.
G-GC is similar to SO. It is big and bulky with a thick jacket. Not what you want in a cramped gutter or something. Maybe you are thinking of type W which is available as single conductor. But I am not sure if the rules allow it as permanent or whatever.
 
Because of the nonstandard circular mil area of DLO, you cannot find DLO ampacities in the ampacity tables. A couple of cycles ago this was added to 310.15 to address that issue.
i dont know about 500, but a couple manufacturers make dlo/rhw in standard sizes, i know ive seen 4/0
 