Birken Vogt
- Grass Valley, Ca
I find that number a hard thing to believe on a house this size. I would run a NEC load calc with all the square footage/equipment/appliances just as a sanity check. You can't allow a generator to overload even once. Realistic worst case as Larry said in #2. All air conditioning running (or heat depending on climate) plus dryer and water heat or anything of that nature all in as much as it is likely to be. Cooking equipment I allow more diversity. Sometimes those demand numbers are spread out over 15 minutes or 60 minutes and may not quite be true instantaneous demand. Or run a worst case simulation on the house with a max logging current clamp.I have the bills for an entire year... all of 2023. The 2 values I provided in post #13 are the maximum demands... I just had them flipped.