Table 310.15b16

Status
Not open for further replies.

Djelite

Senior Member
Location
Ny
Occupation
Electrician
Quick question.Under table 310.15b16 if you go to the 75 degree column. Those insulation type ampacity is rated for 75 degrees even though the actual wire size(copper or aluminum) is rated for an ampacity at 90 degrees continuous. If you are doing ampacity correction you still do ampacity correction at 75 degrees for conductors listed under this column and 90 degrees for conductors listed under the 90 degrees column , correct?
 
Correct. Whatever column the conductor is under is it's derating starting point.
 
The OP was not questioning the weakest part in the chain.
 
The question is not the problem.

The problem is NEC 310.16 ampacity is wrong by itself.
Again you are answering questions that haven’t been asked. The ampacity of the conductor itself has nothing to to do with any other factors. Once you install and terminate that conductor other factors must be considered. But no one is talking about that
 