wc86

Member
Location
Massachusetts
Occupation
Electrician
If i tap into an existing circuit in a house and add 2 receptacles on it can i use a single AFCI receptacle to protect both and be code compliant?(assume its an old panel with no available afci breakers)
 
Look at 210.12(E)
So 210.12(A)(5) is just for new construction and when you extend over 6ft you use 210.12(E) removing the need for metallic wiring method? The only catch after that is you have to locate and replace the 1st outlet and replace it with an AFCI receptacle?
 