ProjectDelta
- Michigan
- Electrician
My company recently had an issue with a temporary installation at a new jobsite where lightning struck a pole feeding the installation and in their investigation, it was determined that the B phase fuse had blown at that pole over a mile away. I've always wanted to see a case study like this to better understand the underlying theory in these situations. I was given the information from the team that troubleshooted the issue and have been analyzing the voltage readings. This is a 13.2kv transformer stepping down to 480v on a delta to wye configuration. The secondary voltages measured are as follows:
A to C: 416V
A to B: 410V
B to C: 99V
A to ground: 273V
B to ground: 149V
C to ground: 143V
These readings where taken under no load condition. Upon review it seems clear now that because the utility B phase was lost, two of the coils are now in series which explains the nearly identical ground undervoltages and if you add the voltage vectors of A coil to B coil and A coil to C coil, the 416V voltages check out. I cant seem to work out the math to explain why B to C is only 99V. Mathematically, the voltage should read 257V. I do have a theory however. Because two of the primary coils are now in series and those both also now in parallel with the A to C coil, perhaps that changes the characteristics of the circuit. Maybe the polarity of the windings impacts the voltage reading. I would appreciate any insight as to how to mathematically prove the B to C voltage. I'm hoping to use this as a case study for my weekly lessons I've started having at our shop for our apprentices. Thank you
A to C: 416V
A to B: 410V
B to C: 99V
A to ground: 273V
B to ground: 149V
C to ground: 143V