hmspe
- Temple, TX
- PE
I do load calculations for many houses that have a calculated load for the whole house significantly less than 400 amps but where the panel calculations for the two panels available for a typical "all in one" do not leave enough capacity in the panels for pool equipment. These are in Arizona so EUSERC applies. The usual solution is to go to a wall hung service with CTs, but the lead times for those are typically over a year.
The Siemens MC3042S1400 series has an integral panel and a second main like a typical CSED, but also has a third space for a breaker tied to the internal bus that is meant to be an input from a parallel energy source. Would it be NEC compliant to use the third main position as a service disconnect to supply a pool panel?