menoknow
- Washington State
- Electrician
Hoping someone can help me understand what I'm not understanding. So let me start by giving a bit of backround. I am about to install some 3 phase 480v pieces of manufacturing equipment, but there have been some questions as to whether or not the utility owned transformer could safely handle the new load. I figured one piece of equipment at (44a x 480v x 1.73 = 36,537W = 36.5kW). installing 10 of these so (36.5kW x 10 = 365kW). So to sum things up 480v 440a 365kW of new load.
However when I gave these figures to the utility engineer he said that I wasn't calculating the kW correctly and that all I needed to do was volts times amps. so just 480v x 44a for total of 21.12kW for one unit. He then told me that I only have to throw in the 1.73 if I'm doing the calculation from 277 volts. However that doesn't really make sense to me since 277v out of a 480/277v system is inherently single phase since as soon as you add another leg it becomes 480v.
Suffice it to say I didn't really argue with him since both his math and my math give me the answer I want which is that there is plenty of room on the transformer for this new installation. However when I did try to dig in a little with him he told me he doesn't actually have an engineering backround, but this is how they all do it in his office. Am I missing something here? I've been browsing the interwebs trying to make sure I'm not wrong in my understanding, and yes I am aware I am leaving out power factor, however I fail to see what I'm missing here. Can somebody possibly help me see what I'm missing here?