Isaiah
- Baton Rouge
- Electrical Inspector
We have 15kV shielded cable (13.8kV system) from an outdoor substation with low resistance ground on the upstream transformer neutral. The associated CT interfaces with a protective relay that opens the line side CB.
Engineering says the circuit needs an EGC (#2/0) for fault current however NEC 250.190(C)(2) states the shield can be used as the EGC if a fault can be cleared without damaging the shield.
I’m just wondering where the relay needs to be set before the fault causes said damage.
Does anyone have experience with this?